On Sat, 18 Apr 2020, Pete Soper via TriLUG wrote:
> Yars ago I instrumented a couple UPS devices to see how the behaved. I recall
> one that was in the wrong county with respect to float voltage. Too low and
> the electrodes accumulate sulphate and die. Too high and the water is
> disassociated and driven past the pressure release as gas, leaving the
> electrolyte short of ions. And the float voltage needs to be temperature
> compensated.
I took out my two APC 700s, in which the batteries only last 2 years.
They have two batteries in series.
On float, one had the batteries at 14.0V and the other at 13.8V. I would accept
anything between 13.8 and 14.4V. I was pleasantly surprised that both batteries
within each UPS had the same voltage within 0.05V (If one goes low, then I
assume the charger will hammer the other one.) The batteries weren't warm, so I
assume the UPS is being nice to them.
So it would seem that these two APC UPS is doing the right thing as far as the
batteries are concerned.
I then took out my unit in which the batteries lasted 10 years.
It has float V=55.0 (4 batteries in a bank. I didn't open it to measure each
battery) = 13.75V/battery.
It would be interesting if a difference in float V of 0.1-0.2V/battery was
making all the difference.
Joe
--